I got this reply from a mechanical engineer friend who specializes...


in heat pump/compressor technology. Before doing any of this, make sure you feel comfortable with working around this kind of stuff, especially in using a volt meter.

1. Is the outdoor fan running and the compressor not? If so you may have a compressor problem.
2. If neither is running check the fuses on the outside disconnect and the breakers in the breaker box. The power supply to the outdoor unit is separate than the indoor unit.
3. If both are good take the panel off the outdoor unit.
4. Check the contactor, is it pulled in? If not manually activate it and see if the unit comes on. If so you have a control (24V issue) or the contactor coil is bad.
5. Check for 24V on the coil of the contactor. If it has 24V the contactor is bad. If not you will have to check the 24V circuit back to the thermostat and figure out why you aren’t getting a call for the outdoor unit. (make sure your unit isn’t on emergency heat only on the thermostat.)
6. If the contactor is pulled in check the output side for voltage. If no voltage is present check the supply side. If there is voltage there the contactor is bad.
7. Some units will actually turn the outdoor unit off if the temperature drops to extremely low levels as you will actually be consuming more power than the heat being provided. If that is the case the outdoor unit will come back on when temps rise (probably >15°F).
8. If from #1 above the outdoor fan is running and the compressor not feel the compressor. If it is hot and you hear it hum occasionally then it’s locked up. If you are good enough with electrical circuits check the capacitor and make sure it is right and with an amp probe check starting currents. Beyond that you will need an HVAC guy to change out your compressor.
9. If you find your compressor is bad and the unit is old and uses R22 strongly consider replacing the whole unit with a new R410A unit.

(In response to this post by MP4VT2004)

Posted: 01/22/2019 at 10:45AM



+1

Insert a Link

Enter the title of the link here:


Enter the full web address of the link here -- include the "http://" part:


Current Thread:
  Update... -- MP4VT2004 01/22/2019 1:57PM
  Still could be....see latest update above. -- MP4VT2004 01/22/2019 2:04PM
  With the flux of replies, a reasonable call. ** -- MikeVT85 01/22/2019 1:55PM
  Or maybe not a problem at all -- 81_Hokie 01/22/2019 12:00PM
  ...220/221 ** -- chumley 01/22/2019 10:39AM
  Whatever it takes. ** -- Hokie CPA 01/22/2019 3:35PM
  Take your thermostat off the wall and check for dust -- hoosnowahokie 01/22/2019 09:26AM
  Blown capacitor ** -- Stork 01/22/2019 09:24AM
  Or a johnson rod ** -- bigbadbird 01/22/2019 09:38AM
  The refs. It's always the refs. ** -- TomTurkey 01/22/2019 10:05AM
  It's the bypass line, not the Fetzer valve. ** -- Spud 01/22/2019 10:01AM
  Guessing on electrical work is usually not worth it ** -- bigbadbird 01/22/2019 09:47AM
  Could be outside breaker if there is one -- bigbadbird 01/22/2019 09:03AM